#1

i was getting some popping noises when my aquahot was on electric only.  kinda like when an element is going bad on a house hot water heater.  

so i bought two new elements from roger berke.   a 120v and 240v.  

with some guidance from rudy, i did the job.

i bought a 12v transfer pump from harborfreight.  and two sockets for the hot water heater.  one is a 1 1/2" impact socket that i had machined so there was no taper on the socket.  since the element nut is so slim, a regular socket will not catch enough on it.  i also bought a camco rv water heater element socket which is not impact worthy but served a purpose i discuss later.  

first i took the burner completely out.  disconnected the fuel lines at the burner as that was the easiest.  you have to take the 4 wires that plug onto the two thermostats above the burner to pull those 4 wires out of the housing as they are attached to the burner.  take a picture of how they are connected.  

then i drained the coolant out the drain hose under the coach.  used a storage bin and then pumped the coolant out into 4 five gallon buckets.  it drains fast and the pump is really fast.  

then took the covers off the elements.  they are both at the bottom.  one at the front and one at the rear.  the front one i just put my 1/2" impact gun on it and it spun right out after a number of hard impacts.  the back element is the 240v one and on mine was a real pain in the neck.  the plumbing back there makes it so i could hardly get my fat hands in there.  i put the impact socket on it with a short extension and used a breaker bar and was able to get it out with some effort.  

replaced the front 120v element was easy.  the back one was not.  it is much longer and heavier and i had to have some way of holding it level to get the threads to start.  so i used the camco socket and put a couple of washers in it, then a couple of pieces of tshirt cloth and wedged the element in it enough to hold it so i could used the socket for leverage.  with a bunch of tries i finally got it.  

then buttoned it all back up and was done.  have not fired it up yet but sure it will be fine. 

the elements ohmed out fine and didnt look very corroded.  the 120v one more than the 240v one.  

i also used my 20mp boroscope and examined inside the tank.  looked pretty clean.  

tom


Attached Files Thumbnail(s)
                       
   

2002 45'8" Newell Coach 608  Series 60 DDEC4/Allison World 6 Speed HD4000MH

Reply
#2

the last picture on my previous post was a picture of the watts mixing valve from the back side. it is a good reference so you know which way to turn it to make it hotter or colder. yes that is my mug in the back....ha

tom

2002 45'8" Newell Coach 608  Series 60 DDEC4/Allison World 6 Speed HD4000MH

Reply
#3

Great job Tom. Hope that stops the popping noises.

Michael Day
1992 Newell 43.5' #281
NewellOwner.com
Reply
#4

Good job! Could the popping noise be the relay? Mine is mounted on right wall above the AH. It was acting weird a few years ago.

Also, the electrical connections under the access door on the front (curbside) of the unit can get loose and start arcing. I had this problem and have seen at least one other. Turn off the power and take off the access cover and inspect the connections. Mine just had a wire nut and when it got loose, it melted and then was arcing against the cover plate.

Rudy helped me fix that one.

Enjoy the hot water!

Bill Johnson
Birmingham, Alabama
Reply
#5

Nice job and writeup. One small upgrade to my aquahot will be to add a 4 wire plug (probably a 4 wire trailer light connector) to the 4 thermostat wires. That will make it easier when I have to pull out the burner.

Forest & Cindy Olivier
1987 log cabin
2011 Roadtrek C210P
PO 1999 Foretravel 36'
1998 Newell 45' #486 

1993 Newell 39' #337 
Reply
#6

it made the noises for the first minute or so it was on and then no more. wont know for sure until i use it alot again.

one thing i forgot to say in my writeup is priming the 4 pumps.

per rudy's guidance, i pressurized the tank using a radiator pressure test setup. i have one so didnt have to go find one. you take the radiator cap off and put the tester on it and pump it up to 15psi.

then turned each of the 4 pumps on one at a time by using a jumper from ground to the terminal block labeled with what thermostat it serves. then leave them on until you can feel the pump priming or feel the coolant pulsing throught the hose above the pump. one of mine wouldnt prime so i tapped the brass check valve just above the pump with a hammer and freed it up. then it primed.

tom

2002 45'8" Newell Coach 608  Series 60 DDEC4/Allison World 6 Speed HD4000MH

Reply
#7

So I just found out (after finally getting the correct j-box wiring squared away that the, new looking, 220v element is no good. I was trying to put off replacing the 120v one until next spring and only use the 220v one this winter, but nope. Have to replace them so I am going to do both.

I've rigged up a pump/drain system, so that will be painless (mostly) however it appears that there is a shutoff valve on the drain line (NOT the little t-handle one at the end) that is oriented in such a way as to obstruct access to the 220v element. 


Any ideas? Anyone else have this secondary shutoff valve to the drain??

Thanks


Attached Files Thumbnail(s)
   

Be seeing you,

Rick Miller
#423
1996, 45'+, Non-slide, Series 60, ABS, 1.5 Bath, Reverse Floorplan


Reply
#8

Couldyou remove the stem to that valve to gain enough room to remove the element?

Guy & Sue
1984 Classic 40' #59
Reply
#9

If removing the stem doesn't work (good idea Guy) you might need to remove that valve. If you do then replace it with a ball valve. Or redo the piping to move the valve further away from the unit.
At a second look if you remove just the red handle would that give you enough room? There should be a screw holding the handle to the stem.

Forest & Cindy Olivier
1987 log cabin
2011 Roadtrek C210P
PO 1999 Foretravel 36'
1998 Newell 45' #486 

1993 Newell 39' #337 
Reply
#10

Looks like I could remove the entire valve stem and valve assembly but leave the housing in place. I will get better measurements tomorrow.

Why would they put the darn thing there in the first place!

Be seeing you,

Rick Miller
#423
1996, 45'+, Non-slide, Series 60, ABS, 1.5 Bath, Reverse Floorplan


Reply