You are not logged in or registered. Please login or register to use the full functionality of this board...


Classic Newell generator blower mystery
#1

Our Perkins  genny shut down due to over heating. We now know that the Murphy Switch protection system works, even after 36 years.  After a good look at the generator system, which I really have not done in 4 years of ownership, I found some things that confuse me. There are some modifications that were done a long long time ago judginging by rust and debris. I know the previous owner well, and am sure that these mods were done before he bought the coach.

The 3/4 120 volt blower motor had blown fuse protection installed (inline) on the incoming hot and common wires about 6 inches from the motor. They are standard automotive 30 amp 30 volt ? Yes 30 volt rated  fast acting blade fuses.

Motor was non op due to the pinching of the 120v lead on the motor frame. Perhaps that was why a prevoius owner had installed fuses on the motor?

The belt pully has been stressed and broken. Before removal I checked belt alignment and it was good, there was no side load.The photo makes it look as though it is not in alignment, but it is right on.  I had noticed cracks in the pully a year ago.

There is no way to adust belt tension. The motor base holes are not slotted.
  
The base area of the cabinet has been cut out with a torch at some time in the past. Maybe to let the air horns mounted inside to be heard?  Smile The motor had a lot of road debris around  it from the hole cut in the floor area  Doesn't this stop the cooling process the same as leaving the  cabinet door open ?

Can one of you Classic guys post pictures of your genny cabinet?

Any and all suggestions are appreciated.


Attached Files Thumbnail(s)
               

Guy & Sue
1984 Classic 40' #59
Reply


Messages In This Thread
Classic Newell generator blower mystery - by Guy - 08-12-2020, 02:05 PM
RE: Classic Newell generator blower mystery - by EArnold3 - 08-12-2020, 02:22 PM
RE: Classic Newell generator blower mystery - by Guy - 08-12-2020, 02:29 PM
RE: Classic Newell generator blower mystery - by Fulltiming - 08-12-2020, 02:39 PM
RE: Classic Newell generator blower mystery - by Tf175 - 08-12-2020, 03:50 PM
RE: Classic Newell generator blower mystery - by bestgenman - 08-13-2020, 05:01 AM
RE: Classic Newell generator blower mystery - by Guy - 08-13-2020, 06:44 AM
RE: Classic Newell generator blower mystery - by Tf175 - 08-13-2020, 10:41 AM
RE: Classic Newell generator blower mystery - by Guy - 08-13-2020, 10:50 AM
RE: Classic Newell generator blower mystery - by Tf175 - 08-13-2020, 11:50 AM
RE: Classic Newell generator blower mystery - by dkarb - 08-13-2020, 12:24 PM
RE: Classic Newell generator blower mystery - by Fulltiming - 08-13-2020, 12:47 PM
RE: Classic Newell generator blower mystery - by Tf175 - 08-13-2020, 05:38 PM
RE: Classic Newell generator blower mystery - by Guy - 09-06-2020, 07:58 AM
RE: Classic Newell generator blower mystery - by Richard - 09-06-2020, 08:39 AM
RE: Classic Newell generator blower mystery - by Guy - 09-06-2020, 09:10 AM
RE: Classic Newell generator blower mystery - by Richard - 09-06-2020, 01:11 PM
RE: Classic Newell generator blower mystery - by Guy - 09-06-2020, 02:25 PM
RE: Classic Newell generator blower mystery - by MrE - 09-06-2020, 04:03 PM
RE: Classic Newell generator blower mystery - by Guy - 09-07-2020, 02:07 PM
RE: Classic Newell generator blower mystery - by folivier - 09-07-2020, 03:07 PM
RE: Classic Newell generator blower mystery - by Guy - 09-07-2020, 05:25 PM

Forum Jump:


Users browsing this thread: 6 Guest(s)