Lost AC power output Kohler 12.5
#2

Is the generator fan working the front right compartment. If so the generator is working the current just isn't getting to the system. Check the 240 volt breakers on the generator. Check the manual transfer switch. There are auxiliary contacts that keep both sets of primary contactors from being activated at the same time. I got some debris in one of mine so it thought the shore power contacts were energized even though they weren't. After cleaning the debris out of the auxiliary contacts, my generator started feeding voltage to the coach again.