09-27-2022, 11:40 AM
Dear Fellow Newell owners, this affects any owner having two piece (basement) AC units. Our coach is # 277, and we just had three failed AC units. The fans had quit.
WW Grainger sells 1/6 hp fans and mounting brackets that with a bit of welding to modify the brackets work great. Anyway, after the fan repairs, two units quit again. What I found was the copper tubing had shifted and rubbed. All the R-22 freon was gone!
There are two fixes after repairing the holes in the copper tubing with silver solder. Make a block (I used wood) and clamp tubing to prevent chafing. Two, use HiTemp RTV (red color) good for 500° and separate the tubing coils and ensure they are supported to remain separate and not rubbing.
Even the screen protecting the compressor can rub through the copper tubing QUICKLY!!!! I have pictures, but seem to post them here. These units used R-22. Newell now used R-422B. Feel free to call or write if you wish more information.
deg ([email protected])
WW Grainger sells 1/6 hp fans and mounting brackets that with a bit of welding to modify the brackets work great. Anyway, after the fan repairs, two units quit again. What I found was the copper tubing had shifted and rubbed. All the R-22 freon was gone!
There are two fixes after repairing the holes in the copper tubing with silver solder. Make a block (I used wood) and clamp tubing to prevent chafing. Two, use HiTemp RTV (red color) good for 500° and separate the tubing coils and ensure they are supported to remain separate and not rubbing.
Even the screen protecting the compressor can rub through the copper tubing QUICKLY!!!! I have pictures, but seem to post them here. These units used R-22. Newell now used R-422B. Feel free to call or write if you wish more information.