Today, I noticed that my L1-L2 120V and 240V indicator lights on the primary electrical panel were off even though I was plugged into shore power. The dash "Shore Power" light was on and the meter's were reading 120V on both L1 and L2.
Starting the Generator and letting it transfer garnered me all the light on properly.
The only thing that is ODD is I am using adapters to go from the 50 AMP 240V shore power cord down to a measly 15 AMP regular extension cord plug (albeit a heavy duty one) Polarity is OK.
I just received the 50 AMP 240V receptacle and will be wiring that up next week, but until then....any reason the lights aren't working?
Thanks,
Be seeing you,
Rick Miller
#423
1996, 45'+, Non-slide, Series 60, ABS, 1.5 Bath, Reverse Floorplan
Posts: 531
Threads: 10
Joined: Mar 2013
A 120 vac, 20 amp power plug is only suppling one leg of a two leg service. It take both legs to have 240 vac, so no 240 vac light.
Rudy Legett
2003 Foretravel U320 4010
ISM11 450 hp Allison 4000R
Factory Authorized Aqua Hot Repair Center
Southeast Texas Area
Posts: 604
Threads: 96
Joined: Jan 2021
Right, but I have NO lights at all.
Be seeing you,
Rick Miller
#423
1996, 45'+, Non-slide, Series 60, ABS, 1.5 Bath, Reverse Floorplan
Posts: 5,752
Threads: 493
Joined: Jul 2012
Very likely the lights could be burned out
Tom
2002 45'8" Newell Coach 608 Series 60 DDEC4/Allison World 6 Speed HD4000MH
Posts: 604
Threads: 96
Joined: Jan 2021
All lights work on generator power.
So not out.
Be seeing you,
Rick Miller
#423
1996, 45'+, Non-slide, Series 60, ABS, 1.5 Bath, Reverse Floorplan
Posts: 1,168
Threads: 28
Joined: Mar 2013
My lights on the overhead panel are a little wonky when plugged into 30 amp in garage. They work great on generator and on 50 amp pedestal at RV parks. But my volt and amp meters work all the time.
Posts: 604
Threads: 96
Joined: Jan 2021
CC,
That's what i was thinking... the weird adapter chain i am using to power it off a 15 amp 120v source might be playing havoc with the lights.
I have a 50 AMP 240v receptacle being installed this week, so will see if it works on that before doing any additional diagnostics
Be seeing you,
Rick Miller
#423
1996, 45'+, Non-slide, Series 60, ABS, 1.5 Bath, Reverse Floorplan
Posts: 5,752
Threads: 493
Joined: Jul 2012
the old neon indicator bulbs go out often. i have replaced most of mine with led
tom
2002 45'8" Newell Coach 608 Series 60 DDEC4/Allison World 6 Speed HD4000MH
Posts: 5,431
Threads: 255
Joined: Jul 2012
Is your adapter chain off the shelf or home made?
Just curious, how do you know the polarity is correct? Looking at the indicator light or checked with a meter?
Richard and Rhonda Entrekin
99 Newell, 512
Maverick Hybrid Toad
Inverness, FL (when we're home
)
Posts: 604
Threads: 96
Joined: Jan 2021
Richard,
The daisy chain adapters are off the shelf Walmart ones from Camco. Polarity at the outlet is checked with a meter.
Be seeing you,
Rick Miller
#423
1996, 45'+, Non-slide, Series 60, ABS, 1.5 Bath, Reverse Floorplan