Posts: 5
Threads: 3
Joined: May 2015
Hi folks
What's the plan of attack when the genny fires up and runs fine, switch is rotated to genny power yet no 110 power. Suggestions? Thanks.
Posts: 5,751
Threads: 493
Joined: Jul 2012
is your generator blower running ok? if so, your generator head is making power.
then i would make sure if there were any breakers on the genny itself that may be tripped.
then go to your transfer switch and see if there is power coming in from the genny.
if there is, then either your transfer switch relays are not working or your switch yourself is bad.
be VERY careful with measuring power. if you are not comfortable doing it with a meter, then find someone to help you
tom
2002 45'8" Newell Coach 608 Series 60 DDEC4/Allison World 6 Speed HD4000MH
Posts: 4,188
Threads: 635
Joined: Jul 2012
Tom is correct. Expanding on a couple of the items he mentioned. If you have a manual transfer switch with a control switch close to the driver to switch between Shorepower and Generator, your transfer switch has, in addition to the two large relays, 2 small relays to prevent accidentally energizing both circuits at the same time. If one of these small relays gets debris in them (they are not sealed), it can cause the transfer switch to fail to switch over. That happened to me once. I turned off the generator, made sure shorepower was not connected, disconnected the inverter, then removed the small relays one at a time and found one with some hay in it. I cleaned it out, reinstalled it and all was well.
I have heard from others that they have had the breakers on the generator itself trip. Resetting the breakers may solve the problem or, if they trip again, indicate and issue with the head on your generator.
Michael Day
1992 Newell 43.5' #281
NewellOwner.com
Posts: 5,751
Threads: 493
Joined: Jul 2012
if the breakers on the generator have tripped, will the blower fan still be running?
tom
2002 45'8" Newell Coach 608 Series 60 DDEC4/Allison World 6 Speed HD4000MH
Posts: 1,168
Threads: 28
Joined: Mar 2013
Check your fuses. We had one go bad that looked good but when checked for continuity found it to be bad. Replaced the fuse (one of the old school glass tube ones) and everything was fine.
Posts: 5
Threads: 3
Joined: May 2015
thanks all, heading out to the coach now to check these out and will keep you posted.
Posts: 5
Threads: 3
Joined: May 2015
breaker was shut off, not sure if it tripped or why, but all is working now. always count on you guys for help, thanks.
Posts: 5,751
Threads: 493
Joined: Jul 2012
glad that was it. hopefully it was a one time event
tom