AC amperage use -
pairodice - 09-03-2024
We still have the original AC units in the coach - whic AC (front or rear) would have the least amount of amperage draw please? We are in a storage bldg with 30-amp service and don’t want to blow the breaker…
RE: AC amperage use -
Richard - 09-03-2024
In theory, they would be the same. Be SURE to set the tstat on low so that only one of the compressors comes on. I know the numbers should support both compressors running, but my experience is the inrush current will trip a 30 amp breaker.
You could also trip the breaker for the second compressor to be sure.