Aquahot Main 12 Volt Fuse - Printable Version
+- Newell Gurus (
https://newellgurus.com)
+-- Forum: Technical Discussions (
https://newellgurus.com/forumdisplay.php?fid=3)
+--- Forum: Heating Systems (
https://newellgurus.com/forumdisplay.php?fid=11)
+--- Thread: Aquahot Main 12 Volt Fuse (
/showthread.php?tid=6937)
Aquahot Main 12 Volt Fuse -
cfree3 - 08-20-2022
We just got back from having service done at Newell where they worked on a number of things however now our Aquahot Diesel Burner will not even attempt to come on. We are assuming it is a main 12 volt fuse for the Aquahot.
We have the 431 and we have already tested all the fuses on the Aquahot and they are all fine.
There must be a main 12 Volt fuse that supplies the 12 volt power to the Aquahot. Looked in the book and couldn't find it listed.
Does anyone know where the main 12 volt fuse is for the Aquahot.
Our electric is working fine so at least we have hot water but we normally use the diesel to heat up in the morning and shut off for the rest of the day.
RE: Aquahot Main 12 Volt Fuse -
Trainer - 08-20-2022
Rick, The main power to the Aqua Hot heater is the big wire in the center of the row of fuses. Check for battery power there. If none, then the protective device on the other end of that wire needs to be looked at. Hopefully an owner can share its location.
If power is there, you have another problem. Get your voltmeter set to DC volts with one lead grounded and call me. We can sort this out by looking for the voltage to run the burner. Where the power stops is the problem.
Rudy Legett 7 one 3 8 one 8 3234